NCO phase drift
I have an NCO generating a 60 Hz sine output.
input clk = 10 khz
phase accumulator precision = 32 bits
angular resolution = 32 bits
magnitude precision = 10 bits
phase increment value = fixed at 25769804
It is a parallel cordic implementation.
My problem is I get a phase drift over time.
I am a new user and would like to understand this better. Any insight would be appreciated.
--- Quote Start ---
--- Quote End ---
Your frequency tuning word is probably being rounded.
Read page 32-34
http://www.ovro.caltech.edu/~dwh/correlator/pdf/esc-100paper_hawkins.pdf
and look at slides 82-86
http://www.ovro.caltech.edu/~dwh/correlator/pdf/esc-100slides_hawkins.pdf
Cheers,
Dave
--- Quote Start ---
--- Quote End ---
Unlikely. NCO implements simple modulo integer arithmetic. The given constant will result in an excact output frequency of 10e3*25769804/2**32 = 60, within the accuracy of the crystal generating the 10k input frequency.
Ignorant question, how do you determine "phase drift over time"? Comparing with mains frequency? Then you'll likely see a "drift".
P.S.: I presume that "drift" doesn't mean the phase jitter of one input clock period.
Thank you for your quick response and information, it is a very good reference.
--- Quote Start ---
--- Quote End ---
Yes I am comparing it with mains frequency. No not the jitter of the one input clock period. The phase of the nco constantly drifts one way or the other. If I increase the frequency of the input clock the drift increases in speed.
It is true that if your tuning word is rounded(in any way) it means phase drift will occur no matter what resolution you use. see my matlab model here:
http://www.dsprelated.com/showcode/240.php
For 60Hz you will need your clock to be integer multiple of 60 e.g. 60KHz and then your modulo can not be power of 2.
You don't need matlab to see, that accumulating the said tuning word of 25769804 with an input frequency of 10e3 results in an exact output frequency of 60. No "rounding" is involved.
10000*25769804 = 60*2**32
The reported problem is apparently related to a frequency deviation of the crystal respectively mains frequency fluctuations.
F.Y.I.: http://en.wikipedia.org/wiki/mains_frequency#long-term_stability_and_clock_synchronization
P.S.: kaz is right about a small rounding. I have been fooled by my pocket calculator. In fact the tuning word is high by about 10 ppb. At least 3 orders of magnitude below expectable crystal accuracy.
The exact tuning word would be 25769803.78
Yes you will get 60Hz "exactly". the issue isn't about frequency but its phase (without affecting frequency due to very slow buildup of fractional error).
the value 25769804 has been rounded and its fraction discarded.
But I suspect in this post the problem is due to clock drift itself rather than NCO drift, however the post has presented itself as NCO problem.
In addition, if the problem is somehow about mains frequency synchronization, an all digital PLL should be considered.
Thank you all for your help...yes the problem is about main frequency synchronization. I have an xor phase detection circuit setup and can implement an all digital PLL which is where this all was going but my concern was if there is a constant phase "drift" the loop would saturate and not be able to control the phase.
If I understood you are trying to lock to the mains 60Hz using NCO.
In this case I assume you will be doing that by changing NCO tuning word up and down from an initial value such that it keeps tracking the mains.
In this case the drift I was referring to does not really apply and the loop should be able to lock provided your ref clock is good enough.
To allow PLL locking in "finite" time, you should allow at least 0.5 or 1 Hz frequency adjustment, I think. The PLL filter has to be designed for a respective lock range in case of an XOR or similar phase detector without frequency comparison
I'm using mains frequency PLLs mostly with "hybrid" (ADC based) analog phase detectors, because typical power electronic related designs involve mains voltage measurement channels anyway.