Two nodes are loaded into the chassis H2224XXLR3,the node Module is iPC – HNS2600BPB24R.

 

In BIOS advance , system acoustic and performance configuration, default value is acoustic, in this case, the system fans always maintains 6K speed, the rear side of the chassis accumulates heat, the CPU1 temperature is very high, the temperature of the optical SFP module reaches above 60 degrees, and can not work properly. But BMC has no alarm prompt.

Modified to performance value, the system fan runs at full speed, more than 13000 revolutions. The voice is very noisy.

Two Xeon silver 4214 processors are configured in the system,firmware version: S2600BP_EFI_BIOSR02010008_ME04.01.04.251_BMC1.93.870CF4F0_FRUSDR_1.39_DCPMM01.02.00.5346

0 项奖励
1 解答
dYu001
新手
1,429 次查看

Dear all: please dont close. We found another strange problem. After updating the whole firmware completely,from the BMC Web we can check that the "exit air sersor" sensor had output data, but when the server lost power supply and restarted power again, the "exit air sersor" sensor status showed Unknown, and the fan speed was not normal.

在原帖中查看解决方案

0 项奖励
7 回复数
dYu001
新手
1,429 次查看

sorry , node Module is HNS2600BPS24R.

0 项奖励
SergioS_Intel
主持人
1,429 次查看

Hello DYu001,

 

Can you please let us know if this problem started after you perform the firmware update?

 

Please install and run the System Information Retrieval Utility (SysInfo) and attach the information.

 

https://downloadcenter.intel.com/download/28712/System-Information-Retrieval-Utility-SysInfo-

 

Also, please let us know if after modifying the values the system temperature decreased.

 

Best regards,

Sergio S.

Intel Customer Support Technician

A Contingent Worker at Intel

For firmware updates and troubleshooting tips, visit :https://intel.com/support/serverbios

 

0 项奖励
dYu001
新手
1,429 次查看

Yes. Normally, after updating firmware, we would install the system and check the health of the system.

0 项奖励
SergioS_Intel
主持人
1,429 次查看

Hello DYu001,

 

We are going to check the log files and will get back to you.

 

Best regards,

Sergio S.

Intel Customer Support Technician

A Contingent Worker at Intel

 

 

0 项奖励
dYu001
新手
1,429 次查看

Intel China engineer jeason.tian help me to find out the error that I modified fru information, resulting in SDR update failure.

we can closed the issue.

0 项奖励
SergioS_Intel
主持人
1,429 次查看

Hello du Yu,

 

We are going to proceed a close this thread as per your request.

 

Best regards,

Sergio S.

Intel Customer Support Technician

A Contingent Worker at Intel

For firmware updates and troubleshooting tips, visit :https://intel.com/support/serverbios

0 项奖励
dYu001
新手
1,430 次查看

Dear all: please dont close. We found another strange problem. After updating the whole firmware completely,from the BMC Web we can check that the "exit air sersor" sensor had output data, but when the server lost power supply and restarted power again, the "exit air sersor" sensor status showed Unknown, and the fan speed was not normal.