S3210SHLC in 3rd party case, fans missing/not monitored sensors in BMC

DAPOS
Beginner
2,369 Views

I have an Intel Server Board S3210SHLC, mounted in a generic 4U rack case.

This board has 4 system fan connectors (besides the CPU fan). All 4 fan connectors are used by generic fans, with 3 pins. The speed of fans are normal.

I have updated the BIOS, BMC, FRU & SDR firmware to the latest versions (S3200SH_BIOS49_BMC39_FRUSDR114).

During the SDR update, i have selected "OTHER" case type, and specified that all system fan are used.

The problem:

If i login to the BMC i get only one system fan (System Fan 3) and the RPM is 0 (zero):

dpccli> sensors -v

04/28/10 | 16:38:41 | BB +1.8V SM | ok | 1.78 | Volts

04/28/10 | 16:38:42 | BB +3.3V | ok | 3.29 | Volts

04/28/10 | 16:38:42 | BB +3.3V STBY | ok | 3.24 | Volts

04/28/10 | 16:38:42 | BB +5.0V | ok | 4.92 | Volts

04/28/10 | 16:38:42 | Processor Vcc | ok | 1.14 | Volts

04/28/10 | 16:38:42 | BB Ambient Temp | ok | 37.00 | Celsius

04/28/10 | 16:38:42 | CPU Fan | ok | 935.00 | RPM

04/28/10 | 16:38:42 | System Fan 3 | ok | 0.00 | RPM

04/28/10 | 16:38:43 | P1 Therm Margin | ok | -68.00 | Celsius

The questions:

How can i monitor all 4 system fans on this board?

How do i activate all fans?

Why there is no speed reading on the only active system fan?

Thank you.

0 Kudos
6 Replies
Edward_Z_Intel
Employee
698 Views

This doesn't look right... Are all fans spinning? A zero RPM reading with "ok" status seems odd to me... Can you try to load FRUSDR again?

0 Kudos
DAPOS
Beginner
699 Views

All fans are spinning just fine.

But i get no reading from them.

I will try to update the FRUSDR again.

0 Kudos
DAPOS
Beginner
699 Views

I have updated the FRUSDR again, selected "OTHER" case, selected all four system fans. Nothing changed.

Still there is only one fan recognized (System Fan 3), with 0 RPM.

If i read the SDR records with SysCfg utility i get the same result, only one system fan is registered (nr 3).

What could it be?

Any ideas?

0 Kudos
Edward_Z_Intel
Employee
699 Views

I tried it on my board by applying SDR again choosing "Other" chassis and select all fans. All fans are showing up in DPCCLI, and connects doesn't has fan readings has 0 RPM reading and "Critical" status. It seems BMC is not getting SDR data correctly. Can you flash BMC again, and then SDR? If still seeing same issue, please try to run http://downloadcenter.intel.com/Detail_Desc.aspx?agr=Y&DwnldID=18895&lang=eng Intel® System Information Retrieval Utility for Windows* and post the result here.

btw, which syscfg command did you use to read SDR records?

0 Kudos
DAPOS
Beginner
699 Views

I will try to flash again the BMC.

The server is running Linux, so i can't run the System Information Retrieval Utility for Windows.

Sorry, i have confused things, i have used the FRUSDR Load Utility (FRUSDR.efi) to read the SDR records, not SysCfg...

0 Kudos
DAPOS
Beginner
699 Views

Today i have managed to "update" again the BMC and the SDR firmware, to the same versions, of course.

By mistake, i have selected during the SDR update, the "Intel(R) Server Chassis SC5299 UP" instead of "Other Chassis".

After the reboot, i have checked the sensors reading in the BMC, and, bang, the system fans are read just fine, but just two of them (SC5299 UP chassis has just two):

dpccli> sensors -v

06/02/10 | 18:56:16 | BB +1.8V SM | ok | 1.78 | Volts

06/02/10 | 18:56:17 | BB +3.3V | ok | 3.30 | Volts

06/02/10 | 18:56:17 | BB +3.3V STBY | ok | 3.24 | Volts

06/02/10 | 18:56:18 | BB +5.0V | ok | 4.94 | Volts

06/02/10 | 18:56:18 | Processor Vcc | ok | 1.14 | Volts

06/02/10 | 18:56:19 | BB Ambient Temp | ok | 32.00 | Celsius

06/02/10 | 18:56:19 | CPU Fan | ok | 867.00 | RPM

06/02/10 | 18:56:20 | System Fan 1 | ok | 3146.00 | RPM

06/02/10 | 18:56:20 | System Fan 2 | ok | 3068.00 | RPM

06/02/10 | 18:56:21 | P1 Therm Margin | ok | -68.00 | Celsius

dpccli>

Next, i repeated the BMC&SDR update and this time i have selected the "Other Chassis" option during the SDR firmware update.Selected all the fans that are installed, update completed and server rebooted.Login to BMC, the update seems that it had worked, all fans are showing:dpccli> sensors -v06/02/10 | 19:19:19 | BB +1.8V SM | ok | 1.78 | Volts06/02/10 | 19:19:19 | BB +3.3V | ok | 3.30 | Volts06/02/10 | 19:19:20 | BB +3.3V STBY | ok | 3.24 | Volts06/02/10 | 19:19:20 | BB +5.0V | ok | 4.94 | Volts06/02/10 | 19:19:21 | Processor Vcc | ok | 1.14 | Volts06/02/10 | 19:19:21 | BB Ambient Temp | ok | 32.00 | Celsius06/02/10 | 19:19:22 | Chassis Fan 1 | ok | 1750.00 | RPM06/02/10 | 19:19:22 | Chassis Fan 2 | critical | 0.00 | RPM06/02/10 | 19:19:23 | Chassis Fan 3 | ok | 3150.00 | RPM06/02/10 | 19:19:23 | Chassis Fan 4 | ok | 3360.00 | RPM06/02/10 | 19:19:24 | Chassis Fan 5 | ok | 3290.00 | RPM06/02/10 | 19:19:24 | P1 Therm Margin | ok | -66.00 | Celsiusdpccli>Now i have to figure out why the Chassis Fan 2 is not read this time (after the first update it was read by the BMC...), because the fan is spinning just fine.Thank you Edward for your help!
0 Kudos