In CRPS power supply document 573090, MFR_MAX_IOUT_CAPABILITY

chunfung
Beginner
1,056 Views

In CRPS power supply document 573090, it listed details about the new "MFR_MAX_IOUT_CAPABILITY" PMbus command.

The Ipeak.max duration value unit should be "ms" or "micro second"?

In document 610445 Eagle stream power supply recommendations, it is using "micro seconds" for Ipeak.max duration.

In CRPS power supply document 573090, it is using "milli seconds" for Ipeak.max duration.

Which is correct?

Labels (1)
0 Kudos
2 Replies
SergioS_Intel
Moderator
1,049 Views

Hello chunfung,


Thank you for contacting Intel Customer Support.


Please allow us to check in your question and we will get back to you as soon as possible. 


Best regards,

Sergio S.

Intel Customer Support Technician


For firmware updates and troubleshooting tips, visit :https://intel.com/support/serverbios


Intel-ScottH
Employee
907 Views

I confirmed with 610445 document, and CRPS owner.

The 610445 is correct, the Ipeak.max duration magnitude is micro-second. the CRPS has a typo.

Reply